Posted 30 June 2020 - 03:26 PM

Not so much that it won't allow charging by solar panels, but that it won't allow charging of the truck battery(ies) by the camper's solar panels. It is a one direction charging device, not a bi-directional device like the later dual sensing ACR/VSR's are.

Oops, didn't see that he said truck battery.


  • 0

#32 Vic Harder

Vic Harder

    Doctor Electric

  • Site Team
  • 4,897 posts
  • LocationCalgary, Alberta

Posted 30 June 2020 - 09:52 PM

Occurs to me that an older, single sensing ACR/VSR wired in parallel with the DC-DC converter and biased towards the truck batteries would allow automagical solar charging of the starting batteries while not interfering with the DC-DC converter's charging of the camper batteries.

 

That's intriguing.  Too bad I chucked my old 1314a in the garbage a while back..... 


  • 1

#33 rando

rando

    Senior Member

  • Members
  • 1,638 posts
  • LocationColorado

Posted 01 July 2020 - 03:23 AM

You would want to be a little careful with putting an isolator in parallel with the DC-DC charger.   With it activated, it would be shorting the output of the DC-DC back to the input of the DC-DC.   If the voltage were to rise enough that the DC-DC thinks the alternator is running, it will switch on - I am not sure what would happen in that case, but a direct short between input and output is probably not a recommended configuration. 

 

If you want to have bi-directional charging you need a double throw relay.   That way it is either DC-DC or direct connection between the batteries, but not both.


  • 0

2016 Fleet Flatbed

2016 Toyota Tacoma


#34 ntsqd

ntsqd

    Custom User Title

  • Members
  • 2,879 posts
  • LocationNorth So.CA

Posted 03 July 2020 - 10:34 PM

Good point. I was making the assumption that the two systems would never normally try to operate at the same time. Mr. Murphy, being who he is and all......

 

If the DC-DC converter has any sort of function indicator it shouldn't be too difficult to create a simple interlock (relay in the ACR/VSR's ground ref wire) so that the ACR/VSR can't operate while the DC-DC converter is operating.


  • 0