klahanie,
Thanks. Yes, I have been looking a lot deeper into this.
Here is my current thinking (pun intended):
I can install a ML-ACR and periodically check my Victron BVM-702 battery manager. Once the batteries move to absorption stage from bulk charging I would use the remote switch for the ML-ACR to disconnect the house batteries and just reply on the solar to finish the charging job. (Thanks to Vic for pointing this out).
The downside is that it is not automatic and idiot proof (I could forget to switch the house battery out of the charging circuit). But it is one heck of a lot cheaper and less trouble than the battery to battery chargers I discussed above. Further, it is not clear to me if the battery to battery chargers can support jumping the starter battery from the house batteries (still waiting for that question to be answered)
As for jump starting the truck diesel via the ML-ACR (or some other device) I got worried when looking at wire size charts and allowable current capacity of wires. My starter can pull from 450 - 700 amps while cranking. Even 4/0 wire is not rated for that amount of current
But then I realized the ratings are for steady state current.
So I found the following equation to calculate the wire size need for short term current.
S =( Ia.√t) / k
Where : S : Conductor cross section in mm2
Ia: Effective (rms/amount of DC current) value of current (A)
t: duration of hazardous shock current (sec.)
k: Cable Insulation Material Coefficient:
For PVC-insulated CU conductors : k=115 As/mm2
For PVC-insulated Al conductors : k=76 As/mm2
For rubber-insulated CU conductors : k=141 As/mm2-
Also I think that the truck battery will be not too far below the starter threshold current need of 450 amps when it is too low to crank the starter so I probably don't need more than 400 amps during jump starting (assuming the truck battery still has 200 - 300 amps or so available).
My truck usually starts with 3 - 4 seconds of cranking but when it is very cold it can take twice that long. I did a calculation using 30 seconds and 400 amps assuming the CU PVC insulated wire and that resulted in a wire cross section of 19 mm2. 4 ga wire has a cross section of 21.1 mm2
My conclusion is that 4 ga would work but 2 ga gives me some margin. I like margin when designing things.
(now I understand why jumper cables which often only have 4 ga wire and are 20 feet long actually work)
P.S: for a non-diesel starter the current requirement is significantly less so my guess is that 4 ga and perhaps 6 ga might be adequate for gas engines.
I hope this is helpful to others following this as well. Also if anyone sees any errors here please comment.
Craig