More on Solar Charge Controllers
Fascinating. I’ve been reading manuals. (And they say men don’t read instructions!!) Lots of manuals, from the manufacturers of charge controllers, both PWM and MPPT types.
Short conclusion: SolarBob is onto something when he says the Trimetric SC2030 is one of the best/smartest controllers out there.
Long conclusion:
1) Most of the manufacturers of less expensive units have unchangeable presets for the various battery types. This is not ideal
2) Even the more expensive and reputable manufacturers (Morningstar/BlueSky/Midnite) use a charging algorithm that assumes your solar panels are sized such that you WILL get a full charge every day, not the actual state of the batteries
a. A “Big enough” solar array is usually 1.5 to 2x watts in your solar array as AH in your batteries. And IDEAL charging conditions.
b. So for 200 AH battery array you would need 300W of solar panels
c. The algorithm is TIME based. As in, charge at this voltage/current for xxx minutes
d. The algorithm should check the voltage and current characteristics of the battery bank to determine if the charging is done, not assume the weather is good
e. Ideally, it would do both C & D.
f. The more expensive units do this: OutBackPower
3) The Trimetric does this, and it is inexpensive to boot
Oh, the other surprise was that you should not mix different solar panels feeding into the same controller.
“Only solar panels of exact or similar current should be wired together in series. When you connect a 3A panel to a 3.5A panel, the overall current will be dragged down to 3A. Such a reduction in current will by all means lead to a reduction in power output and therefore loss in system performance.
Similarly only solar panels of exact or similar voltage should be wired together in parallel. When you connect a 15V panel to a 24 V panel, the overall voltage will be dragged down to 15 Volts. Such a reduction in voltage will lead to a reduction in power output and therefore loss in system performance.” http://solarpanelsve...g-solar-panels/
This means that if you have different types of panels (for your portable and rooftop, or panels added later to an existing array) then you need to have multiple controllers, one for each type.
I know DrJ has had good luck with the EPEVER Tracer A, but those are among the controllers that only charge in the Absorb and Float phases for set amounts of time, not by when the batteries are actually charged.
So I am leaning very strongly towards the Trimetric SC2030 and upgrading my wire sizes if needed.